S Sparky MJ Member Jul 28, 2008 #1 348.42 States that you can't put angle connectors in a wall. Does this apply to MC fittings?
iwire Moderator Staff member Location Massachusetts Jul 28, 2008 #2 Sparky MJ said: Does this apply to MC fittings? Click to expand... Nope. Only applies to a raceways, just like you would not bury an LB in an EMT run.
Sparky MJ said: Does this apply to MC fittings? Click to expand... Nope. Only applies to a raceways, just like you would not bury an LB in an EMT run.
LarryFine Master Electrician Electric Contractor Richmond VA Location Henrico County, VA Occupation Electrical Contractor Jul 28, 2008 #3 Agreed. 348 refers to empty FMC, which is a raceway like conduit is; MC is a cable type.