90 degree connectors

Status
Not open for further replies.

JJWalecka

Senior Member
Location
New England
I have heard that 90 degree connectors are not listed for concealed work. In other words, if removal of building finish is required to access a 90 degree connector it could not be used. Does anyone have facts to agree or disagree with this statement?

JJ
 
The reason is manufactured cable assemblies (AC, MC) vs. a raceway (FMC, LFNC, etc.) Can you imagine trying to repull thru an angled connector concealed in building finish?.....ie. Not accessible.
 
Thank you for your time.
If it is my call I will choose not to use 90 degree MC connectors in concealed work.

JJ

Why? You would never have to pull conductors out of or into a cable assembly.

Roger
 
If at all possible I would try to use a straight connector. Just personal preference.
That's being a little bit short sighted. 90 degree connectors are right handy in a few cases. When fishing MC cable down to an existing box, putting an MC connector on the end to come in a knockout in the back or side of a box is sometimes what you have to do. Also, for appearance's sake (and maybe even to keep the cable from "snapping"), 90 degree connectors are the thing to use to keep exposed cable laying nice. Coming out of a water heater, for instance.
 
That's being a little bit short sighted. 90 degree connectors are right handy in a few cases. When fishing MC cable down to an existing box, putting an MC connector on the end to come in a knockout in the back or side of a box is sometimes what you have to do. Also, for appearance's sake (and maybe even to keep the cable from "snapping"), 90 degree connectors are the thing to use to keep exposed cable laying nice. Coming out of a water heater, for instance.

Well said Marc and agreed.
 
I hope you guys are not using 90 MC connectors with boxes and MC. I don't think the connectors are listed to connect to anything. :wink:
 