And the method depicted below shows what typically must occur to use a conductor at its 90°C-rated ampacity. Everything within the auxiliary terminal enclosure (i.e. "tap box enclosure" is incorrect terminology) is rated for operation at not less than 90°C.

09e_PauleyFIG9.jpg


The only area where I know you can "get away with" not using an auxiliary terminal enclosure is when the "transiition splice" is made inside the rails of cable tray.
 
Last edited:
And the method depicted below shows what typically must occur to use a conductor at its 90°C-rated ampacity.

09e_PauleyFIG9.jpg

There are very few applications where I could see an advantage to doing this, as anywhere where the length is long enough for the benefit to justify the extra complexity, I probably have to curtail voltage drop anyway. But it still does exist in theory, and has some value for correcting a mistake to restore compliance.

The most common reason why one would care about the 90C column of the NEC, is the fact that we can use it for our conditions of use calculations, while using the raw ampacity value at 75C for terminations.
 