wwhitney
Senior Member
- Location
- Berkeley, CA
- Occupation
- Retired
Say you have a feeder between panelboards. Typically at least one end of the ungrounded conductors will landed on a breaker which has max 75C rated terminations. But the grounded conductor may run from one neutral bar to another. Are those neutral bar terminations possibly rated 90C?
If so, you could run, e.g. a 125A feeder with 90C insulated conductors using #1 Cu for the ungrounded and #2 Cu for the neutral, and still have 125A ampacity on the neutral.
Related question: how about the ungrounded conductors on a feeder from feed-through lugs to an MLO panel?
Cheers, Wayne