90C ampacity usable for grounded conductor?

Status
Not open for further replies.

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
Say you have a feeder between panelboards. Typically at least one end of the ungrounded conductors will landed on a breaker which has max 75C rated terminations. But the grounded conductor may run from one neutral bar to another. Are those neutral bar terminations possibly rated 90C?

If so, you could run, e.g. a 125A feeder with 90C insulated conductors using #1 Cu for the ungrounded and #2 Cu for the neutral, and still have 125A ampacity on the neutral.

Related question: how about the ungrounded conductors on a feeder from feed-through lugs to an MLO panel?

Cheers, Wayne
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I don't think that the standard neutral bar in a panelboard is rated higher than 75° C. I've never seen one so labeled.
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
I don't think that the standard neutral bar in a panelboard is rated higher than 75° C. I've never seen one so labeled.
Ah, 110.14(C)(1) tells you that it would have be to "listed and labeled" for 90C conductors. Is there any technical reason to expect it couldn't be so listed and labeled without any actual modifications? Same question for feed-thru lugs and main lugs.

Cheers, Wayne
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
I seem to recall a code change for allowing the neutral to be sized at 90 deg c, that Mike Holt submitted.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
I seem to recall a code change for allowing the neutral to be sized at 90 deg c, that Mike Holt submitted.
I think it said that you don't have to size the grounded conductor at 125% and can size it at 100%. See Exception #3 to 215.2(A)(1).
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
Yes that's correct. The entire assembly would need a 90° C rating.
But does assembly in the above mean "neutral bar," or "panelboard including neutral bar," or "panelboard and enclosure"?

Also, suppose you had a panel where the neutral bar was just going to have a few large connections. Could you substitute a Polaris-style connector rated at 90C? And then if a neutral conductor in a feeder had those at both ends, use that conductor at its 90C rating, despite the panelboard's 75C rating?

Cheers, Wayne
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Since temperature ratings are based on avoiding insulation damage, wouldn't the lower-rated conductor require all conductors in a given raceway to be limited to that lower rating?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
But does assembly in the above mean "neutral bar," or "panelboard including neutral bar," or "panelboard and enclosure"?

Also, suppose you had a panel where the neutral bar was just going to have a few large connections. Could you substitute a Polaris-style connector rated at 90C? And then if a neutral conductor in a feeder had those at both ends, use that conductor at its 90C rating, despite the panelboard's 75C rating?

Cheers, Wayne

My understanding was the entire panel must be rated 90C which IMO, doesn't make sense except that they may be trying to limit the heat that could build up inside the panel.
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
Since temperature ratings are based on avoiding insulation damage, wouldn't the lower-rated conductor require all conductors in a given raceway to be limited to that lower rating?
I guess I'm assuming all the conductors would have 90C rated insulation, so it wouldn't matter within the conduit. The 75C vs 90C ampacity is based on the termination limits, and so part of the question is whether the termination limits can be independent, or if somehow the 75C ungrounded termination temperature precludes having a 90C termination for the grounded conductor, physically within the same cabinet.

Cheers, Wayne
 
I believe if you look at the manufacturer's destructions for the terminations, you will find that no terminal is rated above 75 c,. Even though often the larger lugs are made by a third party and say 90° c on them. I am not sure why this is. Perhaps there is a general restriction in UL 67 the standard for panel boards?
 