Hi
Am I right on this?
If current is continuous you will always have to multiply load current with 125% both for 75C and 90C.
So load of 100A have design current of 125A.
40C amb:
If you choose 75C cable:
125A/0,88 = 142A --> 1/0 AWG
If you choose 90C cable:
125A/0,91 = 138A --> 1 AWG. Check with 75C cable: 125A, no added correction = 1 AWG --> 1 AWG is OK as 90C cable
Thanks