If my #12 thhn is 90C, and the Breaker Im going to be using is 75C do I start my derating at 30 or 25amps? do they make 90c Breakers? thanks
If my #12 thhn is 90C, and the Breaker Im going to be using is 75C do I start my derating at 30 or 25amps? do they make 90c Breakers? thanks
It is a fact: UL does not list any LV (600V max) overcurrent protective device termination for use with the 90?C ampacities.I don't think anyone makes a termination rated for 90c...
There are plenty of 90?C-rated terminations... just none in manufactured assemblies containing distribution or control equipment.I don't think anyone makes a termination rated for 90c. Always thought 110.14(C) should be with the 310. tables. Be less confusing. Just Saying.
You would derate from 30A, get your ampacity, then compare to the 75C column and use the smaller of the two as our final ampacity correct?
In NEC speak, allowable ampacity is the ampacity table value for the conductor....but not necessarily the "allowable ampacity"
In NEC speak, allowable ampacity is the ampacity table value for the conductor.