I am having trouble understanding how to apply 90deg C rating of a conductor to a motor circuit with 75deg termination.
I am dealing with a 550hp motor at 480v so 650 FLA.
We have 90deg C cable for the motor feeder. Using the derating factor given by the installtion site of 35deg C ambient and the 125% requirement for a motor feed the required cable ampacity calculates out as (650 * 1.25)/.96 = 846A. So my cable must be able to carry 846 amps which at 90deg means a parallel set of 500mcm copper.
Now I take into account the 75deg rating of the terminations so I look at 500mcm for 75deg and it is good for 380 amps. This is where I get really confused. The site engineer states that 500mcm are OK to use in this application because the amapcity required is 650a/.96=677 and parallel 500s are good for 730amps after derating for ambient.
Here are the questions I have with this situation:
1. How can you apply the 90deg derating factor of .96 when you are dealing with the 75deg rating (380a)? Shouldn't the ampacity be 650/.94?
2. Why does the 125% motor feeder rule from 430.22 not apply to the 75deg rating? Shouldn't the required ampacity be (650 * 1.25 / .94) = 776 which would bump you to a 600mcm parallel run?
I guess I dont' understand how the terminal rating fits into the feeder sizing, if the terminal is rated for 75deg doesn't that mean that it can only handle 380amps?
I know this is a long post so thank you in advance to anyone willing to get through it.
I am dealing with a 550hp motor at 480v so 650 FLA.
We have 90deg C cable for the motor feeder. Using the derating factor given by the installtion site of 35deg C ambient and the 125% requirement for a motor feed the required cable ampacity calculates out as (650 * 1.25)/.96 = 846A. So my cable must be able to carry 846 amps which at 90deg means a parallel set of 500mcm copper.
Now I take into account the 75deg rating of the terminations so I look at 500mcm for 75deg and it is good for 380 amps. This is where I get really confused. The site engineer states that 500mcm are OK to use in this application because the amapcity required is 650a/.96=677 and parallel 500s are good for 730amps after derating for ambient.
Here are the questions I have with this situation:
1. How can you apply the 90deg derating factor of .96 when you are dealing with the 75deg rating (380a)? Shouldn't the ampacity be 650/.94?
2. Why does the 125% motor feeder rule from 430.22 not apply to the 75deg rating? Shouldn't the required ampacity be (650 * 1.25 / .94) = 776 which would bump you to a 600mcm parallel run?
I guess I dont' understand how the terminal rating fits into the feeder sizing, if the terminal is rated for 75deg doesn't that mean that it can only handle 380amps?
I know this is a long post so thank you in advance to anyone willing to get through it.