R remillard Member Location Bellingham, Massachusetts Jun 5, 2013 #1 Can 90 deg. conn that will end inside the wall be used with MC Cable. I know it's not permissible with flex conduit.
Can 90 deg. conn that will end inside the wall be used with MC Cable. I know it's not permissible with flex conduit.
iwire Moderator Staff member Location Massachusetts Jun 5, 2013 #2 remillard said: Can 90 deg. conn that will end inside the wall be used with MC Cable. I know it's not permissible with flex conduit. Click to expand... For cables yes, for raceways no. When you think of it like that it makes more sense.