R remillard Member Location Bellingham, Massachusetts Jun 5, 2013 #1 Can 90 deg. conn that will end inside the wall be used with MC Cable. I know it's not permissible with flex conduit.
Can 90 deg. conn that will end inside the wall be used with MC Cable. I know it's not permissible with flex conduit.
iwire Moderator Staff member Location Massachusetts Jun 5, 2013 #2 remillard said: Can 90 deg. conn that will end inside the wall be used with MC Cable. I know it's not permissible with flex conduit. Click to expand... For cables yes, for raceways no. When you think of it like that it makes more sense.
remillard said: Can 90 deg. conn that will end inside the wall be used with MC Cable. I know it's not permissible with flex conduit. Click to expand... For cables yes, for raceways no. When you think of it like that it makes more sense.
petersonra Senior Member Location Northern illinois Occupation Semi-retired engineer Jun 5, 2013 #3 <misread>