Hi,

My buddy is planning on wiring a 9kw sauna with a #8 at 240 volts from the panel to the control box and then he says he'll run #12 from the control box to the unit. He says because there are 3 elements each one is 12.5 amps each. Here is the name plate from the heating unit. Is he right?
 

Attachments

  • IMG_6104.jpg
    IMG_6104.jpg
    88.8 KB · Views: 36
What's he doing for the L3 connection? Two elements are doubled up. Can he put two conductors in that lug?
 
What's he doing for the L3 connection? Two elements are doubled up. Can he put two conductors in that lug?
I started to mention that but decided to just state what I did. Most machinery with a control box, you only run total power to it and the control circuit divides it accordingly. I don't know why a user would have to provide internal wiring to something with a control box.
 
Is this thin NRTL listed? Was also wonderin if it needs to be considered a continuous load. At first I thought no, but it has an 8 hour prehet and 4 hour constant heat mode. With a nameplate just over 40A, that puts the continuous load just over 50A so #8 would be a touch too small.

I wish companies would pay attention to load ratings versus wire ampacity limits. Why make a product that draws 40.9 amps. It should have been easy to get it to just just 40A or 39.9A. Same with HVAC heating elements that just barely cross over a wire size.
 
I wish companies would pay attention to load ratings versus wire ampacity limits. Why make a product that draws 40.9 amps. It should have been easy to get it to just just 40A or 39.9A. Same with HVAC heating elements that just barely cross over a wire size.
They may do it so we use the larger conductor.
 