A 2 pole 240 volt Throw switch feeding a 3phase 208 panel.

Mailcall25

Member
Location
florida
Occupation
Electrician
Good day


I have a 240 volt throw switch, in the throw switch it has 4 terminals separated 2x2 on the line side for X1 and X2 only feeding a 208 3 phase panel. So basically, X1 is on one side by itself, and X2, and X3 are one side is it possible for this to overheat conductors, and those conductors are 1/0 .
 
I think he means a knife switch with double lugs on the load side. If that's the case then I think he means A-phase on one side of the 240V and B and C phases on the other side of the 240V. I can't think of a violations, but it's screwy enough that I could be missing something. If it is legal, then the conductors won't overheat, but the total load of B/C phases will be applied to the OCPD.

Mark
 
Good day


I have a 240 volt throw switch, in the throw switch it has 4 terminals separated 2x2 on the line side for X1 and X2 only feeding a 208 3 phase panel. So basically, X1 is on one side by itself, and X2, and X3 are one side is it possible for this to overheat conductors, and those conductors are 1/0 .
🤔
So you're saying two conductors are paralleled?
 
I think he means a knife switch with double lugs on the load side. If that's the case then I think he means A-phase on one side of the 240V and B and C phases on the other side of the 240V. I can't think of a violations, but it's screwy enough that I could be missing something. If it is legal, then the conductors won't overheat, but the total load of B/C phases will be applied to the OCPD.

Mark
I'm guessing a knife switch as well, but your explanation didn't help me either.
The other side of what?
"A" in the left hand hole of the double lug, with "B" and "C" in the right hand hole of the respective lug?
 
🤔
So you're saying two conductors are paralleled?
If I’m reading it right, two of the panel buss’s are paralleled, so one phase is hypothetically 42 space, the other phase is 82 space. If the ocp is correct, it’s not going to overheat, but does have a potential of being very unbalanced. (They are feeding a three phase panel with single phase power)
 
I think he means a knife switch with double lugs on the
If I’m reading it right, two of the panel buss’s are paralleled, so one phase is hypothetically 42 space, the other phase is 82 space. If the ocp is correct, it’s not going to overheat, but does have a potential of being very unbalanced. (They are feeding a three phase panel with single phase power)
load side. If that's the case then I think he means A-phase on one side of the 240V and B and C phases on the other side of the 240V. I can't think of a violations, but it's screwy enough that I could be missing something. If it is legal, then the conductors won't overheat, but the total load of B/C phases will be applied to the OCPD.

Mark
Yes
Picture? I know you know what you said is clear, but I missed something.

A listed product from any of the manufacturers will not increase or decrease the chance of overheating when properly installed and applied.

If I’m reading it right, two of the panel buss’s are paralleled, so one phase is hypothetically 42 space, the other phase is 82 space. If the ocp is correct, it’s not going to overheat, but does have a potential of being very unbalanced. (They are feeding a three phase panel with single phase power)
they are feeding a 208 3 phase disconnect for a condenser
 
I think he means a knife switch with double lugs on the load side. If that's the case then I think he means A-phase on one side of the 240V and B and C phases on the other side of the 240V. I can't think of a violations, but it's screwy enough that I could be missing something. If it is legal, then the conductors won't overheat, but the total load of B/C phases will be applied to the OCPD.

MarkThanks
 
Good day


I have a 240 volt throw switch, in the throw switch it has 4 terminals separated 2x2 on the line side for X1 and X2 only feeding a 208 3 phase panel. So basically, X1 is on one side by itself, and X2, and X3 are one side is it possible for this to overheat conductors, and those conductors are 1/0 .

I think he means a knife switch with double lugs on the load side. If that's the case then I think he means A-phase on one side of the 240V and B and C phases on the other side of the 240V. I can't think of a violations, but it's screwy enough that I could be missing something. If it is legal, then the conductors won't overheat, but the total load of B/C phases will be applied to the OCPD.

Mark
Good day


I have a 240 volt throw switch, in the throw switch it has 4 terminals separated 2x2 on the line side for X1 and X2 only feeding a 208 3 phase panel. So basically, X1 is on one side by itself, and X2, and X3 are one side is it possible for this to overheat conductors, and those conductors are 1/0 .
 

Attachments

  • IMG_8512.jpg
    IMG_8512.jpg
    123.2 KB · Views: 33
  • IMG_8514.jpg
    IMG_8514.jpg
    155.9 KB · Views: 34
  • IMG_8513.jpg
    IMG_8513.jpg
    110.8 KB · Views: 33
I think he means a knife switch with double lugs on the load side. If that's the case then I think he means A-phase on one side of the 240V and B and C phases on the other side of the 240V. I can't think of a violations, but it's screwy enough that I could be missing something. If it is legal, then the conductors won't overheat, but the total load of B/C phases will be applied to the OCPD.

Mark
i unloaded pictures, and i took thermals and it has spots
 