A 40-unit motel (300 sq ft in each unit) has 3 kVA of air-conditioning and 4 kW of heat in each unit, and every two units share one 1.50 kW water heat

Merry Christmas
Location
tuscon Az
Occupation
Engineer
A 40-unit motel (300 sq ft in each unit) has 3 kVA of air-conditioning and 4 kW of heat in each unit, and every two units share one 1.50 kW water heater. What is the calculated load for the motel?

My Calculation - Which maybe wrong..lol (I am wondering what is the use of the 300sq ft in each unit?)

- 4KW (Heater) x 40 units = 160KW
1.5kW/2 units water heater = 1.5KW (20) = 30KW

Water heater = fixed appliance .. so - 30KW times .75 demand factor = 22.5KW

Total = 182.5KW

But correct answer is 202KW

Any help? Ty!
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
No room lighting (this is why sq. ft. matters)? No site lighting? No laundry? No office/house loads?
 

Paul_Briganti

Washington Electrical CEU, LLC
Location
Monroe, WA, USA
Occupation
Educator / VP Electrical Apprenticeship ABC Western Washington
I don't have my 2020 this is based on the 2023 code. Check the VA / Sq. ft. to be sure it is 1.7Va for a motel in your code year.

MLL 300Sq. Ft * 1.7 * 40 = 20400Va
Heat 4000W * 40 = 160000Va
Water heater 1500W / 2 = 750W * .75 * 40 = 22500W

Grand total 202,900Va, if this was to be rounded in Kw it would be 203Kw

This is based on the Standard Method
 