A 40-unit motel (300 sq ft in each unit) has 3 kVA of air-conditioning and 4 kW of heat in each unit, and every two units share one 1.50 kW water heater. What is the calculated load for the motel?
My Calculation - Which maybe wrong..lol (I am wondering what is the use of the 300sq ft in each unit?)
- 4KW (Heater) x 40 units = 160KW
1.5kW/2 units water heater = 1.5KW (20) = 30KW
Water heater = fixed appliance .. so - 30KW times .75 demand factor = 22.5KW
Total = 182.5KW
But correct answer is 202KW
Any help? Ty!