westelectric
Senior Member
- Location
- westchester county, NY
Heres what I have. Min cir amp=20, max fuse 35a, min fuse 30a, rla=15.4
Therefore 15.4x125=19.25a. Is the min cir amp the same as doing that calc? If yes, then #14 @60 deg. is good for 20a. My question is, is all this correct? Is it ok to run #14 and put on 30a c.b. for this single motor compressor (440.32). I think I'm ok doing this. Big savings from #10 to #14.