a/c compressor wire size
westelectric
Heres what I have. Min cir amp=20, max fuse 35a, min fuse 30a, rla=15.4
Therefore 15.4x125=19.25a. Is the min cir amp the same as doing that calc? If yes, then #14 @60 deg. is good for 20a. My question is, is all this correct? Is it ok to run #14 and put on 30a c.b. for this single motor compressor (440.32). I think I'm ok doing this. Big savings from #10 to #14.
Yes it is. You got it correct. But that 20 only applies to certain situation. art. 240.4-- the asterik at the bottom of Table 310.15
is that what the nameplate is saying? if it is the 125% is already multiplied in the nameplate ratings. so i would say u need a #12awg with a 30a breaker
Why? 14 gauge is good for 20 amp.
well i always perceived that the art 240-4(d) says for 14 awg it's rated for 15a, 12awg it's rated for 20a, and 10awg is rated for 30a, unless u r derating or using correction factors for ambiant temps. but i do see the a440-32 but i always thought the 125% is already calculated out for u on the nameplate rating, so u should have to not to do any calc's to that particuler nameplate info. i could be misreading 440-32 wrong.
240.4(D) does not apply here, 240.4(G) does.
You are correct the 125% is already in the namelate for the min. cir amps Art. 240.4(D) It says unless specified in 240.4(E) or (G).... (G) gives the except. for ac units
ok, i didn't read further into a240-4(d), so basically it saying u can use the 60c column for a/c units.
Not really-- it says you can use the 20 amp rating of #14 wire when used for a/c. I think that is what you meant. :D
Dennis Alwon said:
BTW I loved your response on the puck lights. :)
Danke!
Len said:
You cannot put a 30amp cb on #14 wire. You really should get a licensed electrician to properly do work.
If the label says MCA 15a and MOC 30a, you sure can. Note the note at the bottom of Table 310.16.
Len you can put a 30 amp breaker with a #14 branch circuit in certain situations. The a/c is one of them. The unit is protected with an internal overload protection. The 30 amp is only for ground fault or short circuit protection.