a/c condensate pump circuit requirements

dhsvcs

Member
Location
miami
Occupation
electrician
Is there a code requirement that requires a small a/c condensate pump to be on it's own circuit, or can i feed it off a nearby general use ( ltg., power, ect..not bathroom or s.a. circuit ) ? installing power to an new a/c, would use a 120 v condensate pump with a shutdown safety switch...
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
You can supply it from the air-handler circuit or a general-purpose circuit.
:) brings back vivid memories when inspecting and more than once finding the 120v condensate connected to one of the heat strip 30/60 amp breakers and the neutral wrapped around a heat strip mounting screw. ..... "why did I get a red tag"
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
:) brings back vivid memories when inspecting and more than once finding the 120v condensate connected to one of the heat strip 30/60 amp breakers and the neutral wrapped around a heat strip mounting screw. ..... "why did I get a red tag"
I'm certainly not suggesting that. :oops:
 

qcroanoke

Sometimes I don't know if I'm the boxer or the bag
Location
Roanoke, VA.
Occupation
Sorta retired........
:) brings back vivid memories when inspecting and more than once finding the 120v condensate connected to one of the heat strip 30/60 amp breakers and the neutral wrapped around a heat strip mounting screw. ..... "why did I get a red tag"
Isn't it or wasn't it in the code that the condensate pump can't be on the air handler circuit?
 