Please help!I'm very confused after reading all the posts concerning a/c conductor sizing.I have 3 mitsubishi split systems that have been blowing breakers for the outside condensing units.Max fuse size is 20 amps(time delay 20 a fuses at roof top disconnect takes care of that)20a square"d" breaker at panel feeding #12 thhn to disconnect.Can I change to 30a breaker? I have read code book,hand book and many previous posts.Some say yes,some no,some say because outside unit has cooling fan in addition to compressor that I can't.Min. circuit ampacity is 16 amps.Thanks to all in advance.