twilli3967
Member
are you allowed to power the gfci off the disconnect for the a/c or do you need a seperate line to feed the gfci.
not the load sideOriginally posted by twilli3967:
are you allowed to power the gfci off the disconnect for the a/c or do you need a seperate line to feed the gfci.
That is correct.Originally posted by augie47:
I assume they do not come with the recept. pre-wired...only a disconnect and recept mounted in the same NEMA 3R enclosure. Is this not correct?
I would think that if your HVAC is supplied from lets say a 90A 2 pole breaker and you tapped one leg to power the gfci receptacle, you have just installed a 15 or 20 amp receptacle on a 90 amp circuit. To make matters worse, the equipment grounding conductor is used a neutral and a ground. Now you have a ground loop (and perhaps no fault current return path) and you are purposely putting current on the equipment grounding conductor. So now, some poor dude can go up there with his drill, accidentally nick a wire and have 80 amps run through him until the freaking receptacle melts.... some companies were powering them by tapping off the line side and tricked the gfci by using the ground as a neutral and ground. While I know this is not approved under the NEC, wouldn't you have to pull a neutral and also provide some type of ocpd as wel?
It's up to the electrician to avoid temptation to knowingly do something wrong.Originally posted by sceepe:
Looking at the Cutler hammer device, I don't like it. It is way to tempting to just install a little jumper from the terminals for the disconnect to the terminals for the receptacle. (ignoring the fact that you would be putting a 20 amp duplex on a 60 amp branch circuit). Also, it claims to be for residential or light commercial. Probably not beefy enough for my commercial work.
Heres an NEC question. If the disconnect had OCPD for the receptacle and a neutral terminal in the disconnect, would NEC let you tap the 120/208 feed to the HVAC for the recpt?