Would like to know how others size the disconnect, pull out, for A/C's. Do you size for min. or max.? ( min.=16, max=40 )
1793 said:Would like to know how others size the disconnect, pull out, for A/C's. Do you size for min. or max.? ( min.=16, max=40 )
LarryFine said:Steve, you've been throwing money away.
Articles 430 and 440 in the NEC.monsteriname said:Seeins as the original question of this thread has pretty much been answered and some talk has taken place about a related subject that I am interested in I'll go ahead and ask a question if ya'll dont mind.
When sizing circuits,disconnects,switches for motors, the order I should go in is as follows?:
Circuit ampacity if listed on nameplate, FLA if on the name plate, horsepower/output amps as listed on the motor(Horsepower and output amps have to be adjusted, not used as is)
If I have the jist of it what would be some articles to look at that are the exceptions to the above?
Thanks
bphgravity said:I bet nobody can tell me how to size the required disconnecting means for fixed electrical space-heating equipment such as a single family dwelling air handler unit...