jaylectricity
Senior Member
- Location
- Massachusetts
- Occupation
- licensed journeyman electrician
I passed the inspection per the wire inspector, but the building inspector took a look and said he was going to have to give it a "dummy fail" and tell the wire inspector to "revoke" the passing.
Now part of it was that one of the condensers was in front of one of the disconnects. I tried to tell them this when they installed it, but whatever. But he also said the two disconnects were too close together. But on another job we have two disconnects side by side with condensers on either side and that configuration is repeated 10 more times for the other condos in the building.
If the condensers are moved out of the working space area is there any reason why the disconnects can't be right next to each other?
The other thing I noticed is the definitions involved in 110.26. Working space regards equipment, and the definition of equipment seems to include anything with a wire-nut.
Now part of it was that one of the condensers was in front of one of the disconnects. I tried to tell them this when they installed it, but whatever. But he also said the two disconnects were too close together. But on another job we have two disconnects side by side with condensers on either side and that configuration is repeated 10 more times for the other condos in the building.
If the condensers are moved out of the working space area is there any reason why the disconnects can't be right next to each other?
The other thing I noticed is the definitions involved in 110.26. Working space regards equipment, and the definition of equipment seems to include anything with a wire-nut.