Based on that I will go remove all the electric equipment with disconnects mounted in the ceiling of the job I just got a final on.Originally posted by websparky:
Yes. The disconnect would require the 30" minimum and the depth of 36" also.
Article 100404.8 Accessibility and Grouping.
(A) Location. All switches and circuit breakers used as switches shall be located so that they may be operated from a readily accessible place. They shall be installed so that the center of the grip of the operating handle of the switch or circuit breaker, when in its highest position, is not more than 2.0 m (6 ft 7 in.) above the floor or working platform.
Exception No. 1: On busway installations, fused switches and circuit breakers shall be permitted to be located at the same level as the busway. Suitable means shall be provided to operate the handle of the device from the floor.
Exception No. 2: Switches and circuit breakers installed adjacent to motors, appliances, or other equipment that they supply shall be permitted to be located higher than specified in the foregoing and to be accessible by portable means.
Exception No. 3: Hookstick operable isolating switches shall be permitted at greater heights.
In other words all that exception modifies is the accessibility required by 408.8Accessible (as applied to equipment). Admitting close approach; not guarded by locked doors, elevation, or other effective means.
Jim what you are suggesting is that we can pick and choose exceptions from all over the code book to fit.Originally posted by jtester:
I am suggesting that 110.26 is a general rule that applies to equipment in general, 404 is a rule that applies to specific types of equipment, namely switches. It changes some of the general requirements applicable to all equipment. Since the disconnect is a switch, I believe the rules in 110 apply except as modified in Article 404.
Similarly, Article 430 modifies the overcurrent requirements in Article 240, and Article 440 modifies parts of Article 430 even further.
Jim T.
Is there a third option?Originally posted by georgestolz:
Is that a mastery of reasoning or am I retarded?