Confused a bit as to sizing Air Conditioner feeder overcurrent protection -
Let's take a single unit with an RLA of 16 A as an example (assuming no branch circuit selection current is stated on the nameplate). Based on 430.24 the conductors would have to have an ampacity not less than 125 percent of the FLC. Therefore, I would use 12 AWG conductors.
Now, assuming the Max. Fuse Rating is based on 225% as allowed in 440.22(A) the fuses at the disconnect would be rated at 40 A.
Looking at 430.62 it states that the protective device for the feeder shall have a rating not greater than the larges rating or setting of the branch-circuit short-circuit and ground-fault protective device for any motor supplied by the feeder.
So, this would imply the feeder be sized at 12 AWG and have a 40 A circuit breaker. Am I off base on this one?
Thanks,
Jemsvcs
Let's take a single unit with an RLA of 16 A as an example (assuming no branch circuit selection current is stated on the nameplate). Based on 430.24 the conductors would have to have an ampacity not less than 125 percent of the FLC. Therefore, I would use 12 AWG conductors.
Now, assuming the Max. Fuse Rating is based on 225% as allowed in 440.22(A) the fuses at the disconnect would be rated at 40 A.
Looking at 430.62 it states that the protective device for the feeder shall have a rating not greater than the larges rating or setting of the branch-circuit short-circuit and ground-fault protective device for any motor supplied by the feeder.
So, this would imply the feeder be sized at 12 AWG and have a 40 A circuit breaker. Am I off base on this one?
Thanks,
Jemsvcs