My office policy has always been to enter the sum of the compressor RLA and the FLA of any fans as the breaker's load in a panel schedule for a branch circuit to a condensing unit. 25% of the largest motor in the panel is added to the column totals as a separate entry.
I just had a plan rejected by a plans reviewer, who said, at least as I understand it, that the appropriate load to show in a panel schedule for each condensing unit is the MCA. He based this on (1999) 220-14. Before I get too bent out of shape, I though I should ask for comments.
As I see it, 220-14 is for feeders, not branch circuits, so on the face it would not apply. That would put us back at 220-3(b)(1) or 220-3(b)(3). The latter references Article 440, where there's lots of information on conductor sizing, but nothing I can find on what should be used in a load calculation. If 220-14 did apply, the references are to 430-24, 430-25, and 430-26, all of which talk about conductor ampacity, not calculated load.
Comments, please?
I just had a plan rejected by a plans reviewer, who said, at least as I understand it, that the appropriate load to show in a panel schedule for each condensing unit is the MCA. He based this on (1999) 220-14. Before I get too bent out of shape, I though I should ask for comments.
As I see it, 220-14 is for feeders, not branch circuits, so on the face it would not apply. That would put us back at 220-3(b)(1) or 220-3(b)(3). The latter references Article 440, where there's lots of information on conductor sizing, but nothing I can find on what should be used in a load calculation. If 220-14 did apply, the references are to 430-24, 430-25, and 430-26, all of which talk about conductor ampacity, not calculated load.