john warren
New member
I have a a/c condenser with a min. ampacityof 34.5--- using table 310-16 and referencing 240.4(d) exception 240.4(g) ---- looking at 440.6 & 440. 22
Can I use a # 10 thhn conductor size fused at 50 amps?
According to the name plate rating the min ampacity is 34.5 and the max fuse is 50 amps--- As i red it this is totally acceptable
Can I use a # 10 thhn conductor size fused at 50 amps?
According to the name plate rating the min ampacity is 34.5 and the max fuse is 50 amps--- As i red it this is totally acceptable