I'm wiring a rooftop A/C unit with the electric heat option included. The A/C unit is rated at 14.7 amps at 480 volt, 3 phase. Max OCPD 20 amps. The heater is 30 kw. It has two sets of terminals, L4-L5-L6 & L7-L8-L9. Each set of terminals has the same ratings : "Heater Amps : 18.1" , "Heater Ampacity : 22.5" , "Max OCPD : 25". I'm unsure of the difference between "Heater Amps" and "Heater Ampacity", but either way it looks like I need to pull a seperate 25 amp circuit for each set of terminals and a third circuit (20 amps) for the A/C unit. I'm just looking for some confirmation here that I'm looking at it right, but also, I'm wondering if I have any other options since I'm running out of breaker space. Could I pull one larger circuit (60 amps) and then fuse each component seperately at the unit? Or, could I use one circuit to feed both the A/C unit and one set of heaters, since they will not operate at the same time?
Thanks.
John
Thanks.