A/C unit with electric heat

Status
Not open for further replies.

JES2727

Senior Member
Location
NJ
I'm wiring a rooftop A/C unit with the electric heat option included. The A/C unit is rated at 14.7 amps at 480 volt, 3 phase. Max OCPD 20 amps. The heater is 30 kw. It has two sets of terminals, L4-L5-L6 & L7-L8-L9. Each set of terminals has the same ratings : "Heater Amps : 18.1" , "Heater Ampacity : 22.5" , "Max OCPD : 25". I'm unsure of the difference between "Heater Amps" and "Heater Ampacity", but either way it looks like I need to pull a seperate 25 amp circuit for each set of terminals and a third circuit (20 amps) for the A/C unit. I'm just looking for some confirmation here that I'm looking at it right, but also, I'm wondering if I have any other options since I'm running out of breaker space. Could I pull one larger circuit (60 amps) and then fuse each component seperately at the unit? Or, could I use one circuit to feed both the A/C unit and one set of heaters, since they will not operate at the same time?
Thanks.

John
 
I'd say you have it right, yes, you can run a feeder to a sub-panel by the unit, and yes, you can use one circuit for both (maybe). Simultaneous operation must be not possible (under normal operation. Of course, any lockout can be disabled)
 
Here's what I get from your nameplate data:

Heater has two sets of 15 KW elements. Ampacity of each is 18.1 amps(15kw/480x1.73) Minimum Circuit Ampacity is 22.5 amps (18.1x125%) Maximum OCPD is 25 amps.

Sounds like you can choose to use AC, heat with a 15 KW output or a 30 KW output. But knowing this, I'm still thinking about your questions. :confused:
 