I was working on an outdoor A/C unit today, and the nameplate read "16.6 Max current 25A max fuse" does the 125% rule apply to the conductor, or just the brk?
-Eric
-Eric
Mark,The a/c load may not exceed 80% of the branch circuit amps if no other loads are served. If other loads are in the circuit than its 50%.
Originally posted by Mark Beckinger:
I always use a 10-2 wire and a 30 amp breaker.I use 10-2 because there's only a ground terminal anyway.
Circuit breakers provide ground fault and short circuit protection for the conductors only. The OCPD does nothing to protect the motor. The thermal protection in the motor is what protects it.Originally posted by macmikeman:
My theory is that the unit costs somebody big bucks and the breaker at the unit instead of just a disco might save the motor at some point. Of course if the unit is marked for fuse only then there is a fused disconect at the unit.
ocpd- , OVERCURRENT PROTECTION device. I realize that the branch circuit OCPD, is protection enough per 440.52 (A) 3 is enough if there is a disconnecting means provided at the ac unit. Mitsubishi ac compressors have no overloads built in the moter, as far as I can tell. The contactor is just a relay, no heaters. The solid state board might have solid state overload protectors in it but I can see no indications of that in the schematics for these units. There are no clics on devices at the compressor. These machines range in price from about $1500.00 to around $6,000.00 dollars. My load center at the unit adds less than $40.00 to the job. If it trips the circuit on overload due to lock rotor or other problem, I might be saving the owner of the unit quite a bit of dough. I am going to keep using them for the reasons I stated earlier unless you guy's are able to explain better to me why I shouldn't bother.Circuit breakers provide ground fault and short circuit protection for the conductors only. The OCPD does nothing to protect the motor. The thermal protection in the motor is what protects it.
Originally posted by infinity:
Mark,The a/c load may not exceed 80% of the branch circuit amps if no other loads are served. If other loads are in the circuit than its 50%.
I do not believe that this is correct when applied to an AC unit. Do you have a code reference for this?