Dennis Alwon said:Probably so but Cowboys example is not a true example
From the first post
cowboyjwc said:(Some of these numbers are made up so don't do the math)
Dennis Alwon said:Probably so but Cowboys example is not a true example
cowboyjwc said:(Some of these numbers are made up so don't do the math)
Dennis Alwon said:Hey are you telling everyone to ignore my post....:grin:
cowboyjwc said:I don't see this a lot, but I just had a long discussion with an engineer about sizing overcurrent for an A/C unit.
(Some of these numbers are made up so don't do the math)
Min Cir Ampacity = 22amps (which equates to #10 conductors)
Max Fuse or Hacr breaker = 30 (Fused disconnect on roof)
The problem was this.
He had those #10 conductors coming off of a 60 amp breaker saying that he can size the overcurrent 200% and the conductors 125%.
I say that all of the calculations have been done and the overcurrent device cannot be larger than 30 amps to protect the conductors. If he had a nonfused disconnect on the roof the largest size the overcurrent device could be is 30 amps per the nameplate.
Am I missing something?
Jim W in Tampa said:While #12 would be ok i view this two ways,first the run is short so using #10 wouldnt cost me much extra or second is run is long and i would not want voltage drop so get out #10 anyways.
Dennis Alwon said:My point was that it is legal-- that's all.
iwire said:It is not 'legal' in this thread.
The 12 AWG can not be protected with the 60 amp breaker.
iwire said:It is not 'legal' in this thread.
The 12 AWG can not be protected with the 60 amp breaker.
Dennis Alwon said:Secondly, I never said it could be protected by a 60 amp breaker. Read my post I said you could use a #12 wire for a 22 amp a/c load-- I never mentioned the 60 amp breaker.
Dennis Alwon said:Bob, we already made that point and John changed the thread by raising other issues which we are responding to.
Why must you always attack everyone.
Give it a rest will ya.
cowboyjwc said:I think he was trying to use Article 430 for his argument, but he didn't give me an exact code section.
He also used the old "this is only the second or third time anyone has questioned me on this."
Jim W in Tampa said:Then tell him you must be the second or 3rd guy to do his job.I would hope all the electricians out there did not follow his bad advise.We often see mistakes on prints and just fix them.
Minuteman said:Captain Obvious asks - Why a 60 amp breaker? Is that the only breaker in town? Can't we get like, say, maybe, a 30? Or is that thinking to much outside of the box?
wireman71 said:So in this scenario could you use #10, 30amp HACR breaker and a non-fused disconnect? I'm thinking you could.