The breaker that feeds the elevator is not a shunt trip breaker. Is there any reason we can't use a contactor and coil for that would become the shunt?
I can't see why not, just make sure you set it up as fail open, or whatever the AHJ says it needs to be.The breaker that feeds the elevator is not a shunt trip breaker. Is there any reason we can't use a contactor and coil for that would become the shunt?
You cannot use a contactor as a disconnecting means, if that is what you are asking.The breaker that feeds the elevator is not a shunt trip breaker. Is there any reason we can't use a contactor and coil for that would become the shunt?
This is likely the elevator shut down in the event that you're about to get sprinkler activation in the machine room or elevator hoistway.You cannot use a contactor as a disconnecting means, if that is what you are asking.
(B) Operation. No provision shall be made to open or close
this disconnecting means from any other part of the premises.
If sprinklers are installed in hoistways, machine rooms, control
rooms, machinery spaces, or control spaces, the disconnecting
means shall be permitted to automatically open the power
supply to the affected elevator(s) prior to the application of
water. No provision shall be made to automatically close this
disconnecting means. Power shall only be restored by manual
means.
It occurred to me to clarify, in light of what you posted, if you use a contactor you have to make sure there is a manual reset mechanism. You don't want the elevator re-energized as soon as the fire alarm panel is reset.It would appear to me that you are allowed to use the disconnecting means to shut off power if the sprinklers go off but are not required to do so.
So I would say probably the contactor idea is OK.