I think it was the mention of 'sidework' that has folks on edge. The term suggests that you work for an EC, and that this is something you will be doing after hours, behind his back. As you might guess, EC's don't like it when their employees undercut them!
This is certainly something that the apprenticeship should have covered - both in class and on the job. While there's nothing wrong with asking a question, this particular one opens up nearly countless 'what if's' that will vary by the job..
First off, a 'service change' implies everything from the PoCo wires to the branch circuit breakers. It's not just a panel swap. Chances are you'll have to change the meter can- NEC requires a minimum 100 amp service, and some bases are rated only to 60 amps. Let the PoCo disconnect the wires - then reconnect them later. They have their own connectors they like to use.
A larger service means larger wires- which in turn means you get to replace the mast with one that's at least 2" pipe. If your area uses SER, someone else will have to give you pointers.
If there's no grounding electrode (apart from the water bond), you get to bang in a ground rod. Maybe two. How you run the wire from the panel to the ground rod is often specified by the town; ask them.
Your service disconnect will have to rated for the larger service as well. That's where you will 'create' the ground wire- at the neutral lug- if the disconnect is also your main breaker. That, in turn, means you do NOT use the green screw that comes with the panel, and get to mount an additional ground buss. There is no reason that the disconnect needs to be the same brand as the panel.
Nor is there any requirement that you use AFCI breakers. You WILL, however, need to put the circuits that share a neutral on a two-pole breaker, and the breakers need to be the right size. If there was 'double lugging,' or multiple circuits (like the water heater and dryer) "shared" a breaker, you will have to add some breakers.
For you Easterners ... if I've mixed things up a bit, please remember that I typically use "all-in-one" assemblies.