I've had that problem before with natural gas generators, the pipe fitters installed too small of gas line to the unit. Once it got past a certain load, it would shut down due to fuel starvation. Could be a clogged fuel system, but it looks like the generator tech would have checked that, but then the gas unit I had problems with the generator tech missed that. The customer had us monitor the load because the tech said we had a short circuit in our load wiring. The load was staged with two transfer switches, and as soon as the second transferred, the generator would die. After the test, I went out to look at the generator (100 kva three phase) and saw the 3/4" low pressure line ran to it. They replaced it with the proper size, no more problem.