A different option for 680.22(A)

Status
Not open for further replies.

dnem

Senior Member
Location
Ohio
Old
680.22(A)
(1) Circulation and Sanitation System, Location. Receptacles that provide power for water-pump motors or for other loads directly related to the circulation and sanitation system shall be located at least 3.0 m (10 ft) from the inside walls of the pool, or not less than 1.83 m (6 ft) from the inside walls of the pool if they meet all of the following conditions:
(1) Consist of single receptacles
(2)
Employ a locking configuration
(3) Are of the grounding type
(4) Have GFCI protection

(2) Other Receptacles, Location. Other receptacles shall be not less than 1.83 m (6 ft) from the inside walls of the pool.


New/Revision proposal
680.22(A)
(1) All Receptacles, Location. All receptacles shall be located at least 3.0 m (10 ft) from the inside walls of the pool, or not less than 1.83 m (6 ft) from the inside walls of the pool if they meet all of the following conditions:
(1) Employ a locking configuration
(2) Are of the grounding type

Substantiation: . When the 2008 NEC deleted 680.22(A)(4) Restricted Space paragraph that was in the 2005 NEC, any reason to treat circulation and sanitation system receptacles differently than other receptacles was eliminated. . In the 2008 NEC a receptacle located 6? to 10? from the pool must only be twist lock if it is for the pool circulation and sanitation system receptacles. . The circulation and sanitation system equipment is a known variable with a known safety record. . Items powered by the other receptacles are unknown variables with unknown safety and might be handheld and placed on the pool top rail. . The safety of these items should be of greater or equal concern than the circulation and sanitation system equipment.
 