Since an appliance cord would be used "as the crow flies" measurement, I would say the wet-bar receptacle would need to be GFCI protected as long as it's within 6 ft measured along any line,
As far as the bath, 210.8 simply says "bathrooms", so I would say that encompassed ALL.
From an inspectors viewpoint when it involves a relative inexpensive safety item such as a GFCI, I tend to always take the more stringent
philosophy.