hey guys,just wondering if someone can refresh my memory on these two subjects and help me apply the calculations, it has been a while.
motor nameplate rating 11a.
.80x15a ciruit=12a therefore 11a does not exceed 80% of the circuit ampacity, so is this correct a 15a circuit would be fine?
now if the motor will be running for 3 hours or more, would this be correct?
11ax1.25=13.75a So since this now exceeds the 12a(80%of15a), would i go with a 20amp?
i am basically confused on whether to use the 80% rule or the 125% rule. from what i understand, the 80% rule is for motors, and the 125% rule is for continuous load?
motor nameplate rating 11a.
.80x15a ciruit=12a therefore 11a does not exceed 80% of the circuit ampacity, so is this correct a 15a circuit would be fine?
now if the motor will be running for 3 hours or more, would this be correct?
11ax1.25=13.75a So since this now exceeds the 12a(80%of15a), would i go with a 20amp?
i am basically confused on whether to use the 80% rule or the 125% rule. from what i understand, the 80% rule is for motors, and the 125% rule is for continuous load?