Hello everyone, it has been awhile since I have been here and I was hoping to get some feed back on a question that I have.
I have a control panel that feeds a piece of equipment. It is fed with a 50A 480V 3PH circuit. Inside this control cabinet are two transformers. One is a 480 to 120 1.5kva and the other is a 480 to 24v 3kva. Now according to 250.30(A)(4)(a), I need to pull a 3/0 CU grounding electrode conductor to my grounding electrode correct? Or does this particular article refer to service entrance conductors only? I know that Table 250.66 deals with sizing you GEC to the service entrance cables, but does it apply to this scenario? I mean the 250.30 article does not specify control transformers in an enclosure, just multiple separately derived systems.
I have a control panel that feeds a piece of equipment. It is fed with a 50A 480V 3PH circuit. Inside this control cabinet are two transformers. One is a 480 to 120 1.5kva and the other is a 480 to 24v 3kva. Now according to 250.30(A)(4)(a), I need to pull a 3/0 CU grounding electrode conductor to my grounding electrode correct? Or does this particular article refer to service entrance conductors only? I know that Table 250.66 deals with sizing you GEC to the service entrance cables, but does it apply to this scenario? I mean the 250.30 article does not specify control transformers in an enclosure, just multiple separately derived systems.