bphgravity
Senior Member
- Location
- Florida
I've got a question regarding an A/H installation. The garage panelboard contains a 60A circuit breaker labeled for the A/H. A #6 SER cable is installed from this panel to the A/H closet inside the house. The #6 terminates to a 60A panelboard disconnect containing a 60A non-automatic switch (breaker). Form there a short #6 SER whip connects over to the A/H and terminates to a 30A breaker installed in the unit. The A/H rating is 5kW.
Does this violate the code? The unit IS protected by the 30A OCD at the unit, however the branch circuit / feeder is rated at 60A.