joeyww12000
Senior Member
- Location
- Chatsworth GA
Ok I posted a thread yesterday or the day before about bonding and grounding a service. I didnt explain the whole system properly. Still a 600a service. We have an outside utility transformer with service coming undergroung to a 600a disconnect, out to a transfer switch for a generator, neutral is not switched, into building to a MDP with a 600a main breaker, with a couple other breakers to feed other equipment. Right now the 600a disconnect outside has the grounded conductor bonded to the can by a bonding screw and also has a grounding conductor out to a groundrod. Also from the service disconnect outside is ran feeders to mdp where neutral and egc are bonded together inside the mdp. How can the MDP can not have objectionable fault current on it when a fault occurs on one of the panels being fed from the MDP?