a little more derating

Status
Not open for further replies.

arnettda

Senior Member
I have a conduit run that I am derating for. 13 pipes into a j box,out the back and through block wall into a gutter. Out bottom of gutter into top of panel. If nipple through wall and nipple into panel are both under 24" each.I do not have to derate. Would this being permissable? 2 3" pipes through block would be easier than 13 1.5" pipes. wall nipple is 12" and nipple into panel will be about 20".
Do I count each nipple seperate? And is this how the more experienced would do it?
Thanks Dave
 

480sparky

Senior Member
Location
Iowegia
But more CCCs in a larger pipe simply causes more (percentage-wise) derating. If you put, say, 100 CCCs into 13 raceways, you have an average of 7-8 or so in each, and derating isn't that big of an issue since you only derate 70%. If you're installing 14, 12 or 10s, it's a non-issue.

But put those same 100 CCCs into 2 pipes, and you've got 50 per pipe..... Now you derate to 35%, and your cost of copper skyrockets.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
24" or less nipples and no derating is required. The nipple can only be filled to 60%. That's about all the limitations you'll encounter with the installation that you've described.
 