A MAIN BREAKER feeding an ATS, is "LSI" required?

Status
Not open for further replies.

stuartdmc

Senior Member
Does a Main breaker need to be equipped with Digital-trip "LSI" feeding my 200amp ATS from the gen-set?

The main 3000 amp service has a GFP device feeding a SWBD that feeds the ATS, but from the Gen-set there's no GFP, can i use just use a LS trip unit in that breaker?

Using section 215.10 the service is under 1000 amps therefore a GFP isn't required, Correct?
 

steve66

Senior Member
Location
Illinois
Occupation
Engineer
If its a hospital, and you have GFP on the main, you need another level of GFP on the feeders. This is to keep a fault on a single feeder from tripping the main.
 