AndrewG185
Member
- Location
- Chalfont, PA
I need everyone to throw out some ideas because I am stuck on this one. I will try to be as accurate and brief with describing my problem. I am remodeling a kitchen and the existing switch for the kitchen light was powered by a 15amp receptacle in the living room. The outlet is part of a series in the living room, and a wire was simply pig-tailed into the duplex, nothing tricky. I took the duplex out to disconnect the wire, as I ran a new circuit to handle a new series of recessed lights, and noticed that it was damaged so I replaced it with a new 15amp TR duplex. The problem is.....when I connect the neutral to to the duplex from the receptacle upstream, it trips the breaker. With the wires not connected at all, the breaker stays on, if I wire nut the hots and neutrals to each other(respectively) the breaker stays on. When i touch the hot and neutral to a plug, it powers it up no problem. The only thing that trips the breaker is when I touch energized line's neutral to the duplex. I just don't get it. The ground being connected makes no difference, and I am 100% that there is no contacting happening behind the wall outside the box. Ideas?