Good Morning,
ATS 3 pole 4 wire 120/208 volts
Load side of ATS:
Phase A-B 208 volts
Phase B-C 208 volts
Phase C-A 208 volts
A phase to Neutral 120 volts
B phase to Neutral 120 volts
C phase to Neutral 120 volts
A phase to equipment ground 120 volts
B phase to equipment ground 120 volts
C phase to equipment ground 120 volts
Distribution Panel fed from Load side of ATS
Feeder Breaker at the Distribution Panel
Phase A-B 208 volts
Phase B-C 208 volts
Phase C-A 208 volts
A phase to Neutral 120 volts
B phase to Neutral 120 volts
C phase to Neutral 120 volts
A phase to equipment ground 120 volts
B phase to equipment ground 120 volts
C phase to equipment ground 120 volts
Feeder breaker at the Distribution panel that
Feeds panel on the 1st floor, 2nd floor and 3rd floor
1st floor panel MLO feeds thru to the 2nd floor panel
(No breaker in the first floor panel to feed 2nd floor.)
2nd floor panel MLO feeds thru to the 3rd
(No breaker in the 2nd floor panel to feed 3rd floor.)
3rd floor panel MLO.
Now the fun begins
1st floor Panel
Phase A-B 208 volts
Phase B-C 208 volts
Phase C-A 208 volts
A phase to Neutral 95 volts
B phase to Neutral 151 volts
C phase to Neutral 168 volts
A phase to equipment ground 120 volts
B phase to equipment ground 120 volts
C phase to equipment ground 120 volts
2nd floor Panel
Phase A-B 208 volts
Phase B-C 208 volts
Phase C-A 208 volts
A phase to Neutral 95 volts
B phase to Neutral 151 volts
C phase to Neutral 168 volts
A phase to equipment ground 120 volts
B phase to equipment ground 120 volts
C phase to equipment ground 120 volts
3rd floor Panel
Phase A-B 208 volts
Phase B-C 208 volts
Phase C-A 208 volts
A phase to Neutral 95 volts
B phase to Neutral 151 volts
C phase to Neutral 168 volts
A phase to equipment ground 120 volts
B phase to equipment ground 120 volts
C phase to equipment ground 120 volts
Lights dim and flickering
UPS’s in alarm
Patient Monitors shutting down etc… on all three floors
What was going on for work…Removing the over bed patient room lights.
In those lights are a normal branch circuit and an emergency branch circuit separate from each other. Including the neutral.
How the situation temporarily was corrected…
Go back to each of the patient room lights that were removed
And connect the neutral from the normal branch circuit to the neutral of the emergency branch circuit. And everything went back to normal. ?????
Which is not normal.
Any ideas or thoughts….Thank You
ATS 3 pole 4 wire 120/208 volts
Load side of ATS:
Phase A-B 208 volts
Phase B-C 208 volts
Phase C-A 208 volts
A phase to Neutral 120 volts
B phase to Neutral 120 volts
C phase to Neutral 120 volts
A phase to equipment ground 120 volts
B phase to equipment ground 120 volts
C phase to equipment ground 120 volts
Distribution Panel fed from Load side of ATS
Feeder Breaker at the Distribution Panel
Phase A-B 208 volts
Phase B-C 208 volts
Phase C-A 208 volts
A phase to Neutral 120 volts
B phase to Neutral 120 volts
C phase to Neutral 120 volts
A phase to equipment ground 120 volts
B phase to equipment ground 120 volts
C phase to equipment ground 120 volts
Feeder breaker at the Distribution panel that
Feeds panel on the 1st floor, 2nd floor and 3rd floor
1st floor panel MLO feeds thru to the 2nd floor panel
(No breaker in the first floor panel to feed 2nd floor.)
2nd floor panel MLO feeds thru to the 3rd
(No breaker in the 2nd floor panel to feed 3rd floor.)
3rd floor panel MLO.
Now the fun begins
1st floor Panel
Phase A-B 208 volts
Phase B-C 208 volts
Phase C-A 208 volts
A phase to Neutral 95 volts
B phase to Neutral 151 volts
C phase to Neutral 168 volts
A phase to equipment ground 120 volts
B phase to equipment ground 120 volts
C phase to equipment ground 120 volts
2nd floor Panel
Phase A-B 208 volts
Phase B-C 208 volts
Phase C-A 208 volts
A phase to Neutral 95 volts
B phase to Neutral 151 volts
C phase to Neutral 168 volts
A phase to equipment ground 120 volts
B phase to equipment ground 120 volts
C phase to equipment ground 120 volts
3rd floor Panel
Phase A-B 208 volts
Phase B-C 208 volts
Phase C-A 208 volts
A phase to Neutral 95 volts
B phase to Neutral 151 volts
C phase to Neutral 168 volts
A phase to equipment ground 120 volts
B phase to equipment ground 120 volts
C phase to equipment ground 120 volts
Lights dim and flickering
UPS’s in alarm
Patient Monitors shutting down etc… on all three floors
What was going on for work…Removing the over bed patient room lights.
In those lights are a normal branch circuit and an emergency branch circuit separate from each other. Including the neutral.
How the situation temporarily was corrected…
Go back to each of the patient room lights that were removed
And connect the neutral from the normal branch circuit to the neutral of the emergency branch circuit. And everything went back to normal. ?????
Which is not normal.
Any ideas or thoughts….Thank You