Hi there, I wondering if is normal that a transformer shows decreasing values of DGA, we do analysis yearly. We got these numbers:

GAS201420152016
H2132312122617424
H2O52021
CO2251522893624104
Thanks a lot beforehand. Regards
 

wbdvt

Senior Member
Location
Rutland, VT, USA
Occupation
Electrical Engineer, PE
It has been awhile since I have been involved in DGA but I believe the oil temperature plays a part in how much gas is in the oil. I doubt that all the samples had the same oil temperature. I would be more concerned with the water in oil amounts. Is pressure being maintained in the transformer?
 

Bugman1400

Senior Member
Location
Charlotte, NC
There is a lot of info missing. Some of the question I have are:

1.) Is this xfmr new in 2014?
2.) What were the values on the test report at the manufacturer?
3.) Has the oil been dried or filtered?
4.) What are the units of measurement for the values you've given (ie ppm)?
5.) What is the size an voltage of the xfmr?
6.) Is this xfmr in El Salvador where its humid and the water count would be higher than say in Arizona, US?
 