AdrianWint
Senior Member
- Location
- Midlands, UK
My employer makes educational products... amongst them a full time supersonic wind tunnel. The wind tunnel is powered by vacuum pump driven by a 50kW 2 pole 400V motor (I'm UK, so this is 400V line-line 3 phase 50Hz land)
We buy-in the vacuum pump/motor as a package but the control system is our problem. That's fine, I'm competent & happy to design this, but I do have a question for some of the more experienced motor/inverter guys that reside on this learned forum.
The previous builds have used a soft-start to control the motor start-up current. For practical reasons (the amount of spare capacity we have in the factory being one) I've setup the soft-start to throttle the start current at around 250A. This leads to a run-up time for the motor pump of around 20-25s before the current falls back to its running current of around 60A per phase and the soft start comes off line. Since the supply to the factory is only 400A/phase (and the normal loading is around 250-280A/phase) I've always insisted that we run this machine outside normal hours (by killing non-vital load, we can take the 'quiet' factory consumption to around 60-70A/phase) removing any risk of taking out the main supply fuses.
However my Masters have decreed that the Customer wants training on this product and it must be run during normal working hours. On previous builds I discovered, empirically, that if I throttle the current back below about 200A the motor can't accelerate upto 3000 rev before the max start time of the soft-start is exceeded & the unit trips out. I'm not comfortable pulling an extra 250A on top of the normal factory load (even for that 20-30s or so) and feel that the risk of taking out the supply fuses is too great (If they do open, 90 people will be sat around twiddling their thumbs until power is restored by the Utility).
So, here is the question.... If I swap the soft-start for a full blown inverter drive, what would this do to the mains supply current needed to get this pump up-to speed? Will it be nearer the 60A/phase or so that that is needed during steady running (hence I could fire this up during normal factory hours) or will I still be looking at start currents in the 200-300A region??
(There is no requirement for the pump to run at anything other than 3000 rev.... this is purely a 'need the min possible start current' problem)
Thanks for your input
Adrian
We buy-in the vacuum pump/motor as a package but the control system is our problem. That's fine, I'm competent & happy to design this, but I do have a question for some of the more experienced motor/inverter guys that reside on this learned forum.
The previous builds have used a soft-start to control the motor start-up current. For practical reasons (the amount of spare capacity we have in the factory being one) I've setup the soft-start to throttle the start current at around 250A. This leads to a run-up time for the motor pump of around 20-25s before the current falls back to its running current of around 60A per phase and the soft start comes off line. Since the supply to the factory is only 400A/phase (and the normal loading is around 250-280A/phase) I've always insisted that we run this machine outside normal hours (by killing non-vital load, we can take the 'quiet' factory consumption to around 60-70A/phase) removing any risk of taking out the main supply fuses.
However my Masters have decreed that the Customer wants training on this product and it must be run during normal working hours. On previous builds I discovered, empirically, that if I throttle the current back below about 200A the motor can't accelerate upto 3000 rev before the max start time of the soft-start is exceeded & the unit trips out. I'm not comfortable pulling an extra 250A on top of the normal factory load (even for that 20-30s or so) and feel that the risk of taking out the supply fuses is too great (If they do open, 90 people will be sat around twiddling their thumbs until power is restored by the Utility).
So, here is the question.... If I swap the soft-start for a full blown inverter drive, what would this do to the mains supply current needed to get this pump up-to speed? Will it be nearer the 60A/phase or so that that is needed during steady running (hence I could fire this up during normal factory hours) or will I still be looking at start currents in the 200-300A region??
(There is no requirement for the pump to run at anything other than 3000 rev.... this is purely a 'need the min possible start current' problem)
Thanks for your input
Adrian