mshields
Senior Member
- Location
- Boston, MA
Now that I've received a reply; here's what was on my mind.
517.34 list loads for the Equipment branch of an EES. Autoclaves are listed under (B)Equipment for Delayed Automatic or manual Connection, (6) and reads "Minimal electrically heated autoclaving equipment shall be permitted to be arranged for either ..."
My question is, what is meant by "minimal electrically heated"
i.e. what is the added meaning of those three words. if you eliminated them it would read that "Autoclaving equipment shall be permitted to be arranged for ...
What does this qualifier do to the intent of the sentence?
Thanks,
Mike
517.34 list loads for the Equipment branch of an EES. Autoclaves are listed under (B)Equipment for Delayed Automatic or manual Connection, (6) and reads "Minimal electrically heated autoclaving equipment shall be permitted to be arranged for either ..."
My question is, what is meant by "minimal electrically heated"
i.e. what is the added meaning of those three words. if you eliminated them it would read that "Autoclaving equipment shall be permitted to be arranged for ...
What does this qualifier do to the intent of the sentence?
Thanks,
Mike