david
- Pennsylvania
I have just recently attained my ICC certification for electrical inspector and hope to be starting new job soon. I have been doing lots of research in the 2017 NEC and the IRC. My question relates to mobile home service conductor sizing. After the meter if one uses a Mobile Home disconnect with the usual 4 circuits, and let's say they come out of there to get the well pump and the outside condenser. Now let's say this is a 200 amp service. From the disconnect into the mobile home wouldn't you be required to use 3/0 copper which would make your incoming service conductors 3/0 since no feeder conductor can be larger than incoming service conductor. It seems to me you can't use the 83 percent here because the disconnect with the circuits. Everyone around here uses 2/0 in this example. Thanks
When a manufacture tags a home the manufacture of the home has declared the calculated load of the home. In the manufacturer’s instructions or on the tag it states 200 amps. The instruction state by table 200-amp 3/0 copper feeder.
The home has a service panel in the basement or on a pole adjacent to the home. Sometimes the service panel is attached to the outside of the home.
The manufacture’s instructions apply to the feeder.
If a distribution panel is installed for such loads as a pad mount HVAC unit or a shed or well pump. The service needs to consider these as additional loads to the manufactures load calculation
For a 200 amp manufactured home a 200 amp service with additional breaker spaces intended for additional loads would be undersized