I recently had a temp power inspection, and the inspector informed me that effective on my next installation, the way I had installed it will fail inspection. I've since sent him an email after our conversation to get more details about where this change is coming from, but in my opinion it's a step in the wrong direction. The installation was performed as follows:
Underground feeders (4/0 - 4/0 - 2/0 - 6) were installed between a service rated 200A meter pedestal and a 200A Feed Through Exterior load center. The structure had a ufer ground and a building steel ground connected on a continuous conductor, with no neutral bond at the feed through panel. The neutral bond exists at the meter pedestal, which also has a ground rod.
The meter pedestal also has 4 breaker spaces (in addition to the 200A breaker and terminals), one of which will be feeding a well house, and the other, a barn subpanel. Both of which also have equipment grounds, with the barn having two new ground rods.
The change I was instructed to follow is this: remove the equipment ground from between the pedestal and building disconnect, the pedestal and barn disconnect, and install a bonding jumper at the building disconnect and barn disconnect.
It is my opinion, after looking through the definitions of feeder and service equipment in article 100, and then looking at 250.32(B)(1), that the installation as instructed would be a violation.
I'm still waiting for a reply that provides any local amendments that may contradict this interpretation.
All of this goes without saying that I believe this creates some major safety issues, especially in the event of a lost neutral. In my opinion it goes against the intent of a ton of code changes over the past couple decades, and everything I know about safe grounding and bonding practices.
I'm interested to hear any opinions on this subject, or some enlightenment on details I may be missing.
Underground feeders (4/0 - 4/0 - 2/0 - 6) were installed between a service rated 200A meter pedestal and a 200A Feed Through Exterior load center. The structure had a ufer ground and a building steel ground connected on a continuous conductor, with no neutral bond at the feed through panel. The neutral bond exists at the meter pedestal, which also has a ground rod.
The meter pedestal also has 4 breaker spaces (in addition to the 200A breaker and terminals), one of which will be feeding a well house, and the other, a barn subpanel. Both of which also have equipment grounds, with the barn having two new ground rods.
The change I was instructed to follow is this: remove the equipment ground from between the pedestal and building disconnect, the pedestal and barn disconnect, and install a bonding jumper at the building disconnect and barn disconnect.
It is my opinion, after looking through the definitions of feeder and service equipment in article 100, and then looking at 250.32(B)(1), that the installation as instructed would be a violation.
I'm still waiting for a reply that provides any local amendments that may contradict this interpretation.
All of this goes without saying that I believe this creates some major safety issues, especially in the event of a lost neutral. In my opinion it goes against the intent of a ton of code changes over the past couple decades, and everything I know about safe grounding and bonding practices.
I'm interested to hear any opinions on this subject, or some enlightenment on details I may be missing.