A two 2 pole breakers connected together?? and feeding two seperate panels

Status
Not open for further replies.

Cartoon1

Senior Member
Location
Florida
Occupation
Electrical Engineer
Hello! I came across this today and I have not experienced it before. There was (two) 2 pole breakers connected togethor. The main panel (feeding the whole campus, a bunch of small buildings) is 120/240 1 phase 300Amp M.C.B.. The (two 2 pole breakers that are connected togethor) are feeding two seperate small buildings, those buildings panels have each their own 150A MCB interior panel that feeds its building. I verified that by turning this breaker off and those two separate buildings went off. my question is why they didnt use seperate two 150A breakers. Are they both sharing the 150Amps? See attached pictures. Any knowledge on this would be appreciated. Thank you
 

Attachments

  • a1.jpg
    a1.jpg
    384 KB · Views: 46
  • a2.jpg
    a2.jpg
    152.9 KB · Views: 46
  • a3.jpg
    a3.jpg
    257.7 KB · Views: 45
That is a single 2 pole 150A branch breaker.

I believe the QO plug on jaw is rated a maximum of 125A so Square D uses a factory assembly of (2) 2-pole housings to handle higher ampacities. Note how only one housing has printed information on it.
 
That is a single 2 pole 150A branch breaker.

I believe the QO plug on jaw is rated a maximum of 125A so Square D uses a factory assembly of (2) 2-pole housings to handle higher ampacities. Note how only one housing has printed information on it.
Is that code compliant? If i wanted to add another breaker to this panel would i able to add another 150 or even a 200 amper with the same setup?
 
Is that code compliant? If i wanted to add another breaker to this panel would i able to add another 150 or even a 200 amper with the same setup?
You're only limited by what the manufacturer says is the largest breaker that can be supplied by the connection to the bus stabs. If Sq D allows a 200 amp CB in this panel then you can use one.
 
They had to make something that fits the space where other breakers mount that can handle the higher current.

Not as good of a chance of making some variant of one of these fit there.

1652272065187.png

Variants of that do exist for use in I-line panels though.
 