A 120/208v-3ph-4w A/V Panel is fed from a separately derived "isolation" T/F--
the T/F will be grounded per 250-30. A/V plans call for the A/V Panel to be grounded back to the building service equipment with a #4 AWG-Cu. Question: Is that additional #4 EGC violating NEC? / or would that just be a "supplementary" ground?