ptonsparky
Tom
- Occupation
- EC - retired
200 HP irrigation pump motor.
We ordered a 753 set up with enclosure and all the goodies. It is configured as a 2 wire control and includes an HOA that uses a DI "Run" in Hand, and the same DI Run in the Auto via a N/O contact that we supplied. Auto also does a PI Enable via another DI.
Speed control is via a 0-10v pot when in Hand and a 4-20 ma in Auto.
We are getting a Fault Code 5 while in the Auto. I associate this with a short deceleration ramp time. We are supposed to be Coast to Stop, but I will have to confirm that is selected for both Modes. (Those making the changes have not given me a complete list.)
Baring that oops, would too tight of a PID loop cause this problem? We have a 3% deadband.
The motor does not seem to hunt for speed and sounds pretty quiet.
Note: The motor does run into the SF amps at 60 Hz and no doubt has ran there since installed some years ago.
We ordered a 753 set up with enclosure and all the goodies. It is configured as a 2 wire control and includes an HOA that uses a DI "Run" in Hand, and the same DI Run in the Auto via a N/O contact that we supplied. Auto also does a PI Enable via another DI.
Speed control is via a 0-10v pot when in Hand and a 4-20 ma in Auto.
We are getting a Fault Code 5 while in the Auto. I associate this with a short deceleration ramp time. We are supposed to be Coast to Stop, but I will have to confirm that is selected for both Modes. (Those making the changes have not given me a complete list.)
Baring that oops, would too tight of a PID loop cause this problem? We have a 3% deadband.
The motor does not seem to hunt for speed and sounds pretty quiet.
Note: The motor does run into the SF amps at 60 Hz and no doubt has ran there since installed some years ago.