Abandoned Cable

Status
Not open for further replies.

czars

Czars
Location
West Melbourne, FL
Occupation
Florida Certified Electrical Contractor
The NEC Index lists a number of cases of abandoned cables and the actions required (Cables, Abandoned). Is there a requirement to remove other abandoned cables such as old NM cable in an attic or an abandoned two conductor dryer cable in a cement block wall when a new 3 conductor cable is installed?
 
No, there is no requirement for your scenarios.

Roger
 