Don800.52(B) ... The accessible portion of abandoned communications cables shall not be permitted to remain.
Abandoned Communications Cable. Installed communications cable that is not terminated at both ends at a connector or other equipment and not identified for future use with a tag.
Don't forget the tag.Originally posted by steve66:
So I don't have to remove any cable that has RJ45 connectors left on both ends? That seems simple enough.
Steve, I read termination as connected to a piece of equipment. (like a wall outlet, server or something similar.) Just having RJ45 on both ends might and not labeled, might not "qualify" as termination. For future use, just having a piece with a connectors with no tag might cause problems for you later.Originally posted by steve66:
Steve
The definition states;Originally posted by kfenn:
An RJ45 is a connector, no more needs to be done.terminated at both ends at a connector or other equipment
No that is not correct.Originally posted by steve66:
The way I read the definition, if a cable has connectors OR labels, it is NOT abandoned. Is that right? You have to use boolen logic to read that definition.
If Not A = Not B And Not C then:
A = B or C.
Programmers must write the NEC![]()