abandoned wiring

Status
Not open for further replies.

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
It is only the low voltage cables that are addressed, I believe. They must be either removed or labeled for future use. One example is 725.25.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
You need to be more specific as the the type of abandoned wiring. Power and lighting conductors are permitted to remain without tagging. Removal or tagging would apply to Class 1,2,3 wiring, fire alarm wiring, CATV, fiber optic cables, communications cables and probably a few more that I left out. You can check each of those articles for the specific code sections.
 