I have an ABB circuit breaker that has an electronic trip unit that needs to have its trip setting changed while it is in the ON position.
The breaker is an ABB, SACE-S4 250 amp breaker with a SACE PR211 trip unit.
The setting that needs to change is the L longtime setting from 0.4 (100a) to 0.6 (150a).
Will the breaker trip when making this change and will the sensor use the correct value without turning the breaker off to make the change?
This is on a UPS that has been upgraded and the UPS tech forgot to change the breaker settings so now they need to be changed while the unit is online.